Assuming a 50 amp load, if #8 wire is used there is a 0.512 volt drop, if #6 wire is used there is a 0.32 volt drop. Change the breaker & leave the #8 wire, imho.
:beer:
:beer:
You most likely know your numbers way better then me but could you show or tell me the math you used to get those numbers?moi said:Assuming a 50 amp load, if #8 wire is used there is a 0.512 volt drop, if #6 wire is used there is a 0.32 volt drop. Change the breaker & leave the #8 wire, imho.
:beer:
Zum said:You most likely know your numbers way better then me but could you show or tell me the math you used to get those numbers?moi said:Assuming a 50 amp load, if #8 wire is used there is a 0.512 volt drop, if #6 wire is used there is a 0.32 volt drop. Change the breaker & leave the #8 wire, imho.
:beer:
I'm not being sarcastic,just wanting to know.
Using this site;
https://www.powerstream.com/Wire_Size.htm
I am way higher,same with the minn kota site.
For the length of wire would you(/do you?)put 20 / 40 feet.moi said:Zum said:You most likely know your numbers way better then me but could you show or tell me the math you used to get those numbers?moi said:Assuming a 50 amp load, if #8 wire is used there is a 0.512 volt drop, if #6 wire is used there is a 0.32 volt drop. Change the breaker & leave the #8 wire, imho.
:beer:
I'm not being sarcastic,just wanting to know.
Using this site;
https://www.powerstream.com/Wire_Size.htm
I am way higher,same with the minn kota site.
No problem, I used the chart/calculator on this site. https://www.stealth316.com/2-wire-resistance.htm
Easier than doing the calculation.